Critical - MM: Short-term increasing temperature rate of change violation
Posted: Mar 3, 2010 5:54 PM
 
Click to report abuse...   Click to reply to this thread Reply
we use the APC environmental manager

looks like someone just installed this version of the apc environmental manager and now we are getting:

Critical - MM: Short-term increasing temperature rate of change violation

the data center is fairly cool, what sensor can I disable or change the settings on to stop this message from coming up
i picKed a winna


Posts: 2,079
Registered: 10/18/07
Re: Critical - MM: Short-term increasing temperature rate of change violation
Posted: Mar 4, 2010 5:25 PM   in response to: ikeleong in response to: ikeleong
 
Click to report abuse...   Click to reply to this thread Reply
what part number do you have? AP9340 and AP9320 are the likely SKUs..I am thinking AP9340 because it says MM (main module) but just want to be sure..

with that, someone can assist you in what specific settings to change.

if its an AP9340, in the web interface, check under Sensors->whatever temp sensor name you want to change->Rate of change settings.

once you click on that, you can adjust the short term increasing settings.
Legend
Platinum Medalist: 3001 - 9999 pts
Silver Medalist: 2001 - 3000 pts
Super User: 1600 - 2000 pts
Guru: 1199 - 1599 pts
Advisor: 798 - 1198 pts
Specialist: 397 - 797 pts
Freshman: 0 - 396 pts
Helpful Answer (5 pts)
Correct Answer (10 pts)

Point your RSS reader here for a feed of the latest messages in all forums




Powered by Jive                                             
Forums